Navien Error Code F9: Line voltage too low or too high (AC)

Updated · by Aurora Star Tech Inc.

Navien error code F9 on a air conditioner means: Line voltage too low or too high. It is also called Navien diagnostic code F9.

High severityAir ConditionerNavien NAA

Homeowner? What Navien code F9 means for you

Call a technician Your air conditioner is reporting: Line voltage too low or too high. The air conditioner has locked out or cannot run properly. One reset is fine; if the code comes back, it needs a licensed technician to find the cause.

Safe things you can check yourself

  • Check the thermostat: right mode (Heat or Cool), set a few degrees past room temperature, and fresh batteries if it uses them.
  • Check both breakers and the outdoor disconnect box beside the outdoor unit; all should be ON.
  • Look at the air filter. If it is grey and clogged, replace it; a blocked filter causes many shutdowns.
  • Keep about 2 feet around the outdoor unit clear of leaves, grass and debris.
  • If you see ice on the pipes or the indoor coil, turn the system off and run only the fan for a few hours, then call a technician.
  • Try one reset: turn the power off for 30 seconds, then back on. If the code comes back, stop resetting and call a technician.

Call (647) 657-2977Book a service call

Licensed technicians serving Vaughan, Toronto and the GTA.

What does Navien error code F9 mean?

The board saw supply voltage below 172 V or above 275 V. Normal supply is 230 V.

Applies to: NAA17V36 (24K/36K), NAA17V60 (48K/60K)

Common causes of Navien code F9

  • Low or high supply voltage
  • Loose line wires at the terminal block
  • Outdoor PCB fault
Safety: Gas, electrical and refrigerant work must be done by a licensed technician. Turn off power and gas before servicing, never bypass a safety control, and always follow the manufacturer's manual for your exact model.

Navien models that use code F9

NAA17V36NAA17V60

Other Navien AC codes

CodeMeaning
F1Low pressure switch fault
F4T4 outdoor ambient sensor fault
F5T5 compressor discharge sensor fault
F6T3 condenser coil sensor fault
F7T7 sensor fault
F8T7 sensor: condensate risk on the cooling plate
FAOutdoor board memory (EEPROM) fault
FBDrive chip memory (EEPROM) fault
FCDrive module temperature sensor fault
FDPressure sensor not detected
FET3 or T5 probe out of position
FFHigh pressure switch reads open all the time

All Navien Air Conditioner error codes →

Navien code F9: homeowner questions

What does Navien code F9 mean?

Line voltage too low or too high. The board saw supply voltage below 172 V or above 275 V. Normal supply is 230 V.

Is it safe to keep using my air conditioner with code F9?

It depends on the cause. The air conditioner has locked out or cannot run properly. One reset is fine; if the code comes back, it needs a licensed technician to find the cause.

Can I reset Navien code F9 myself?

You can try one reset (power off for 30 seconds, then on). If Navien code F9 comes back, the cause is still there and a licensed technician should check it.

Who can fix Navien code F9 near me?

Aurora Star Tech Inc. repairs Navien air conditioners in Vaughan, Toronto and across the GTA. Call (647) 657-2977 or book a service call online.

Homeowner help: AC Running But Not Cooling: What to Check

Troubleshooting guides

Source: Navien NAA Series Air Conditioner Service Manual, 3.2.3, p.24. Written in our own words as a summary; always check the original manual.

General guidance for qualified technicians. The manufacturer's installation and service manual and local codes always take priority. Aurora Star Tech is not affiliated with, endorsed by or sponsored by any equipment manufacturer; brand and model names are used only to identify equipment and belong to their owners.